What is VFD, and how its work
Answers were Sorted based on User's Feedback
Answer / guest
VFD is variable frequency drive.Its varies frequency of
applied it,its use for variey speed of AC MOTORS
| Is This Answer Correct ? | 4 Yes | 0 No |
Answer / chinmaya
VFD is variable frequency drive.It is used for regulating
the RPM of a motor by regulating it's frequency.
| Is This Answer Correct ? | 4 Yes | 0 No |
Answer / abhishek goyal
VFD: Variable frequency drive
Input supply: 3phase AC 440V, 50HZ
Output: 3phase AC 440V, variable freq.
VFD is the speed controlling device for motor by using
frequency method OR V/F Method. In VFD 3phase ac supply
change into the DC and after the dc supply can control or
change by IGBT into 3ph ac supply. it can be change
frequency by triggering the IGBT gate by given supply
voltage to gate. According to gate activation it can change
or convert ouput supply into variable or desire supply.
| Is This Answer Correct ? | 2 Yes | 0 No |
Answer / nipesh sathavara
VFD is variable frequency drive.It is used for Speed control of motor with current control.As Maintain by V/F ratio.
| Is This Answer Correct ? | 1 Yes | 0 No |
Answer / venkat iyer
VFD is known as Variable Frequency Drive, and is used in AC Electrical System for varying the speed of a 3 phase squirrel cage induction motor, by varying the output frequency of the drive. The AC voltage is initially converted into DC and the energy / POWER is stored in capacitors which is later inverted through IGBT (insulated gate bypolar transistor)
| Is This Answer Correct ? | 0 Yes | 0 No |
why trasformer rated in kva why should have to maintain pf in our site 0.9
What are the tests to be taken on a transformer and generator?
how maney type tempereture measurement ?
Can Anyone suggest the Standards (IEC or IS) for selecting copper current density?
My load is 1635 KW. & current pf is 0.884, I have to improve it for 0.99.Please suggest what KVAR value is needed?
What is effect on in zone and out zone fault if CT chosen for phase side is Vk/2<5mA and Neutral side is Vk/2<15mA on REF protection of Transformer
what is the working principle of soft-starter & how it diff. from VFD ?????????
How to find the maximum load that can supply by a particular(say 315kva) KVA rated transformer?
Going in for a three phase motor or a single phase motor, what factor should be considered for this? For eg., to pump water to certain height and such domestic applications, which motor is suitable?
How to calulate Voltage Drop for perticular lentgh of busbar (Cu/ Al)?
when we put inducter in neuteral grounding of genrator.
What value(high/low) of diversity factor is desired in power system and why? How such value is achieved?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)