why we use primary delta connectin in hight voltage transformer
Answers were Sorted based on User's Feedback
Answer / abhishek-gaur
in DELTA connection, phase voltage = line voltage
in STAR connection, phase voltage = 1/(root3) times line
voltage
to reduce losses, transmtng voltag should be higher, so we
use delta connectn.
bcoz star connctn wil reduce phase voltg to 0.707 times line
voltg...
thus voltg is lowered wid star ... and losses incresed
compard to delta
Is This Answer Correct ? | 3 Yes | 0 No |
Answer / satheesh
to prevent zero sequence current flow in upstream side.
Is This Answer Correct ? | 3 Yes | 2 No |
What test must you do before powering up a circuit that you have been working on?
in slip ring motor if motor specification is given how we calculate its rotor resistance in starting
How to calcluate the current by means wires/cables in square mm
what is a universal motor? how it works?
why we step down voltage level from 33kv to 11kv and 11kv to 415v.Instead we can step down voltage from 33kv to 415v directly using single transformer?
what is power frequency withstand and impulse withstand of a circuit breaker?
What is the distance between each insulator in 33kv transformer and how can it calculate
What is the RMS Value. Please discribe in detail
what is p.s impedance measurement test in earthing transformer?
Why Neutral Earthing pits and body earthing is interconnected
On load tap changer (OLTC) explode? Transformer Vector group: Ynd11 Rated Power: 353MVA Rated Current: 693A Voltage:294/20KV OLTC Type: T III Y1000 110/c 12193w Max Operation Current: 295A Step Voltage: 550V Arrangement in Tx windings: Y Connection Problem: Damage of Unit 1 Generator Transformer On Load Tap Changer (OLTC) Description of Incident: 9.00 a.m. :- Generator No Load test on excitation system started 10.30 a.m :- Carried out AVR change over test 11.30 a.m :- Preparation for Generator Manual Synchronizing test 12.00 a.m :- Manual Synshronizing test started. Observed incoming generator voltage higher than running voltage. CECR operator operated Generator Transformer OLTC to bring down the incoming generator voltage 12.03 a.m :-Generator Transformer abnormal alarm operated at Gen.Control Desk (CECR) CECR operater at Generator transformer bay informed that the transformer oil splashed out from OLTC. CECR operater informed that he heard explosion inside OLTC. Observed Oil level & Oil Flow alaram operated at Tranformer local annunciator. 12.05 am :- CECR operator 'Open Gen Field Breaker” 12.10 a.m. :- Elec1 team inspected the OLTC and found the OLTC rupture disk was broken and oil spilled at OLTC area. - Elec1 found the OLTC top cover bulging. Do anyone know why and possibility cause happen in this OLTC.
WHY STABILIZER SHOULD USED