Answer / sms

AS PER IS:6792 , Oil Electric break down voltage( BDV) at
room temp using 2.5 mm gap should be Min 30 KV .
Accordingly don't take risk and carry out oil filteration
as early as possible to avoid any break down.

Is This Answer Correct ?    2 Yes 1 No

oil sample dielectric test gives the insulation rupture voltage at 26 kv. is this transformer saf..

Answer / k.prakashchandra

40 KV is the minimum value required. You need not panic.
Measure the BDV again after 15 days. If there is drop ,oil
filtering is to be done at the earliest

Is This Answer Correct ?    1 Yes 1 No

Post New Answer

More Electrical Engineering Interview Questions

What is technical difference between ELCB & ELMCB?

3 Answers  


Why USe In -48 DC Volt !

3 Answers  


please mention the minimum IR value for different voltage systems

6 Answers  


how to decide the rating of the ct for 1500 kva transformer

1 Answers  


in an open circuit. test there is no load curent.. but secondary. ia open then no urrent have to flow but there a smaller current flows why?

4 Answers   Rubber Park,






how to test the electrical panel.ht lt mcc pcc.

0 Answers   Ambience, Shivalik,


where can the transformer having vector group Yny0 be used??

0 Answers   GK Power, NEA, Petrotech,


On what principle reluctance motors work?

1 Answers  


What is block diagram?

0 Answers  


When testing an earthing connection, we use a 60 or 100 candle bulb with a phase connected direct from supply and the other wire to the new earthing provided.If the bulb glows then the earth is ok.Else earth connection is not Ok. So, why dont we can use all the home appliances taking a single wire from the phase and the return connection to Earth instead of return connection to neutral?

2 Answers  


What is meant by time harmonics and space harmonics?

0 Answers  


Does Rheostat can use for power factor correction?

1 Answers   GOMS,


Categories
  • Civil Engineering Interview Questions Civil Engineering (5085)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4451)
  • Electrical Engineering Interview Questions Electrical Engineering (16632)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)