oil sample dielectric test gives the insulation rupture
voltage at 26 kv. is this transformer safe to be operated .
The working voltage is 11 kv
Answers were Sorted based on User's Feedback
Answer / sms
AS PER IS:6792 , Oil Electric break down voltage( BDV) at
room temp using 2.5 mm gap should be Min 30 KV .
Accordingly don't take risk and carry out oil filteration
as early as possible to avoid any break down.
Is This Answer Correct ? | 2 Yes | 1 No |
Answer / k.prakashchandra
40 KV is the minimum value required. You need not panic.
Measure the BDV again after 15 days. If there is drop ,oil
filtering is to be done at the earliest
Is This Answer Correct ? | 1 Yes | 1 No |
What is technical difference between ELCB & ELMCB?
Why USe In -48 DC Volt !
please mention the minimum IR value for different voltage systems
how to decide the rating of the ct for 1500 kva transformer
in an open circuit. test there is no load curent.. but secondary. ia open then no urrent have to flow but there a smaller current flows why?
how to test the electrical panel.ht lt mcc pcc.
where can the transformer having vector group Yny0 be used??
0 Answers GK Power, NEA, Petrotech,
On what principle reluctance motors work?
What is block diagram?
When testing an earthing connection, we use a 60 or 100 candle bulb with a phase connected direct from supply and the other wire to the new earthing provided.If the bulb glows then the earth is ok.Else earth connection is not Ok. So, why dont we can use all the home appliances taking a single wire from the phase and the return connection to Earth instead of return connection to neutral?
What is meant by time harmonics and space harmonics?
Does Rheostat can use for power factor correction?