what is difference between E/P positioner and I/P positioner.
Why E/P fixed in below actuator and why I/P fixed in other place
Answer / carl_ellis
An E/P transducer is a voltage to position transducer, so
its input signal from the control system is a voltage
signal, like 0-5Vdc. Its output is a proportional pneumatic
signal.
An I/P transducer is a current to position transducer, so
its input signal from the control system is a current
signal, like 4-20mA. Its output is a proportional
pneumatic signal.
E/P and I/P are not positioners and are not called
positioners because each is a transducer that converts an
input signal to a proportional pneumatic signal.
A positioner is a much more than a transducer; a positioner
is a controller.
A positioner senses valve position and regulates its
pneumatic output to control the valve position to the
setpoint defined by the input signal.
Where an E/P or an I/P is mounted is a matter of opinion,
plant standard or convenience, it is not dependent on its
function.
A positioner must receive a valve position feedback signal,
so a positioner must be mounted so mechanical linkage can
sense valve position or when mounted remotely from the valve
(like in high ambient temperature applications) a remote
position sensor is used to feed a signal to the positioner.
Carl Ellis
Measure First
| Is This Answer Correct ? | 3 Yes | 0 No |
what is the difference b/w magnetic flow meter&mass flow meter? which one is best?
what is maximum vaccume?
How a conductivity sensor & analyzer work at boiler, whats the principle & science is beyond this,How conductivity sensor sence & convert signal & move toward analyzer & analyzer show reading in percent? also what is temperature compensate option in conductivity analyzer
what are the pinciples & units of flow, level, temperature, pressure, quality.
How much flow is passing through 6 inch line? There are no gauge, no any transmitters in line.
Name different parts of a pressure gauge.
On LPG sphere tank we used LIT for level indication.High side port is connected to the bottom of the tank while low side port connected to the top. I would like to know how to fill the glycerin on its low side with two condensing pot installed,one from top and the other one for its drain line.Please I need your expertise...thanks
what master plc do?
how to do loop checking pls email to shanavaska2000@yahoo.com
what is the calibration procedure for transweigh make weigh feeder?
whats the abbreviation of IOP? is it instrument of power or input open problem?
Condensation within a sight glass? Would you expect there to be more problems when using a sight glass if there is condensation on the inside or the outside of the glass, and why?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)