What is the reason for not giving very High Proportional
Gain Kp in PID Controller?
Answers were Sorted based on User's Feedback
Answer / deepti
A high proportional gain results in a large change in the
output for a given change in the error. If the proportional
gain is too high, the system can become unstable (see the
section on loop tuning). In contrast, a small gain results
in a small output response to a large input error, and a
less responsive (or sensitive) controller. If the
proportional gain is too low, the control action may be too
small when responding to system disturbances.
Is This Answer Correct ? | 35 Yes | 0 No |
Answer / www.islamqa.com
Great answer Deepti
and also with increasing the Kp gain we increase the MAX.
OVEERSHOOT of the process which may harm the process and
lead to unwanted consequences.
Regards,
Ahmed Sabry
Control and Instrumentation Engineer
GPC - General Petroleum Company
ahmedsabry.online@gmail.com
CELL.: 00 2 0121367310
Is This Answer Correct ? | 6 Yes | 2 No |
what is the full form of psig.
Explain the functions of the CPU of a PLC.
WHAT IS THE CAM POSITION IN CONTROL VALVE POSITIONER ? WHY IT IS USED?
if temperature transmitter is showing wran. sensor 2 fail how can you remove from the transmitter display m/n.3144p rosemount
Dear all... I have 1 0-400 duplex type RTD, I connected the A side to the temperature indicator and B side to the PLC panel, but when I have observed then found that The PLC side temp has the variation. and it was distub to other RTD temp also. so what can I do.pls help me
WHAT IS THE MASS FLOW FLOW METER
what will be the pressure in tank which has the total level of 2 meters and is filled 1.2 meters ?
What is ALSPA 370 control system
1 Answers DUBAL-Dubai Aluminium,
What is controller? What is transmitter?
we have a s-5 simense plc having op7 .recently on op7 showing error 1.plc not present 2. DB error frequently. can u have any solution . please send me.
How the flow can be measured by using DP Transmitter?
What is NODE in DCS?