what is difference between earth fault& restricted earth
fault.
Answers were Sorted based on User's Feedback
Answer / k.prakashchandra
EFR is for general earth fault and REFR is for earth fault
within the area covered or for a certain equipment e.g.
tranformer.
Is This Answer Correct ? | 5 Yes | 4 No |
EF/SEF/50N/51N/51G can be detected by core balance CT or by vector summation of line CT(residual)
64REF is by comparing current flowing at TR neutral CT with residual CT at line CT,
Is This Answer Correct ? | 0 Yes | 0 No |
Answer / harnish desai
REF will detect earth fault within its equipoment & work on
principal of vector sum of Ir + Iy + Ib + In = 0.
Ef relay will sense current in only neutral CT & operate
relay.
Is This Answer Correct ? | 0 Yes | 1 No |
How Load Factor, Demand Factor, Diversity Factor etc best applied in designing an electrical circuit? Is it allowed to consider these factors in each and every panel in an electrical distribution system? Can any body suggest a good book for reference?
What does Bode plot tell you?
why current increases when voltage decreases in ac system
what is role of mpu in dg
If we impress a dc voltage of 230 V on an unloaded 230 V, 50 Hz transformer it wi A give high secondary voltage B burn out C give secondary voltage as per K D none of these
if we supply DC power to AC transformer then what its result?
Why tripping not occur when the transmission breaks? Doesn't we provide earthfault protection for it?
i HP = ?? 746 watts or 735.5 and how??
how to calc. current for 5MVAR,50hz,33kv
What will be the voltage impact on secondary side of two transformers with different vector groups when both voltages are compared.
what is the diff. between AVR & H.T.Stabilizer
what is meant by rotating magnetic filed