generator(Deutz 550kv)is runing for 2 hours with load of
900 amp and then it goes in shutdown with alarm fault
messege of speed fault although heirtz reading fixed at
50,what does that mean
Answer / k.prakashchandra
Gen voltage can not be 550 KV which I think ,is the tr
voltage. Hz is at 50 even after gen has tripped.That
means ,it was connected to grid.The gen might have tripped
on over speed due to load throw-off. If not, speed sensor
of the gen is to be checked
Is This Answer Correct ? | 0 Yes | 0 No |
IR value for 30kw lt motor
what happens if power factor is maintained at 0.9?give me the answer in technicall way rather than telling the penality n all
what should be correct gas pressures to be a 1.5 ac unite
testing of Vector Group – YNaoD II
In a 3 phase system a neutral exists so that any unbalanced currents can flow through it towards earth.... but a phase demands a particular current as per the load attached to it....then where does the extra current come from the goes in the neutral??....I mean in an unbalanced system a phase demands a current as per its load attached....then where does the unbalanced current come from??