generator(Deutz 550kv)is runing for 2 hours with load of
900 amp and then it goes in shutdown with alarm fault
messege of speed fault although heirtz reading fixed at
50,what does that mean
Answer / k.prakashchandra
Gen voltage can not be 550 KV which I think ,is the tr
voltage. Hz is at 50 even after gen has tripped.That
means ,it was connected to grid.The gen might have tripped
on over speed due to load throw-off. If not, speed sensor
of the gen is to be checked
| Is This Answer Correct ? | 0 Yes | 0 No |
Please brief working principle & construction of permanent magnet AC Servo motor
HOW TO CALCULATE HV TEST VOLTAGE FOR ELECTRICAL EQPT.
Why the CT Secondary is rated as 5A generally?
1.main parts of generator? what is used A-check,B-check,C- check? 2.what is FM200 system in data centers? 3.difference between pac,ahu?
highest rating of alternator used in india
Which motor connection is preferable star-delta or delta-star?
How the line trap works in substation...?
can we keep open the secondary of current transformer?
why we use four type of phase angle difference between pimary & secondry winding of a transformer & where we use them?
why do we need a 4th wire in 3phase 3wire transmission line
What is partial discharge in power cable?
A 3PH MOTOR RUNNING IN NORMAL CONDITION AND ITS AMPERE ALSO UNDER ITS FULL LOAD CURRENT,ITS CABLE RATINGS ALSO HIGER THN ITS CAPACITY,BUT ITS CABLE GETTING ABNORMAL HEAT(NOT TOO HOT)WHY ITS GETTING HOT LIK THIS
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)