what will be fault level of 11 KV , 2000 A ELECTRICAL
SYSTEM?
Answers were Sorted based on User's Feedback
fault level depends on your system's percetage impedance.In
general practice we are using 28KA for 3 secs. or 40KA for
3 secs.
Is This Answer Correct ? | 1 Yes | 0 No |
Answer / genau
Mr. Ranjan is correct!!
Fault level of the system will depend on the system impedance.
for calculation of fault level, calculate the fault impedance and hence you can calculate fault current from system voltage and fault impedance. product of two gives fault level in VA (Generally specified in MVA)
Is This Answer Correct ? | 0 Yes | 0 No |
what is ground fault in ACB?
Diffrectiate between earthing and neutral
why not starting switch first connect in direct on line starter?????
how to calculate the cable size depending on the amps?
What is Negative Potential Bias
ADVANTAGES OF DIGITAL COMMUNICATION OVER ANALOG.?
will we get shock from dc?
testing ZNYn11(d) vector group transformer
what is the meaning of knee point in current transformer and how to calculate?
what is the difference between ac and dc?which one is more efficient?and what r their advantages
why do we need to use 3c+3e cable, normally i select only 3c+e cable and i think it is enough. pls explain the usefull of 3e cable ( in this project the earthing system is well done)
How to increase the specific gravity of DG batteries?