Answer / sunil ulange hit nidasohi
Sort circuit MVA= Rating * 100 / Z%
Short Circuit Current =Short circuit MVA / 1.732* Voltage
Is This Answer Correct ? | 7 Yes | 3 No |
Answer / karuppannasamy
Rated primary current=2000/(1.732*33)=35A
Short circuit current= Rated current/Impedance
= 35/.075=466A
Similarly
Rated secondary current=2000/(1.732*11)=105A
Short circuit current=105/.075=1400A
Is This Answer Correct ? | 2 Yes | 4 No |
Answer / madhu
Fault impedance in secondary Z = %Z x 10 x (KV)²/KVA
= 7.5*10*11*11/2000
= 4.5 OHMS
then fault current in sec = V/(Z*1.732)
= 11000/(4.5*1.732)
= 1411 A or 1.4kA
similarly in primary Z = 7.5*10*33*33/2000
= 40.83
then fault current in prim = 33000/(40.53*1.732)
= 0.466kA
Is This Answer Correct ? | 0 Yes | 3 No |
Megar test tell sufficient resistant
Why the starting current in Induction Motor is very high as compared to normal rated current ????
what is ATS & RING MAIN UNIT in Distribution System?And its Function.
what is the difference between squirrel cage & slip ring induction motor by construction & working principle ?
what is mathed of check the D.C MOTOR 181 KW (ARMATURE AND FIELD) WHAT IS THE MATHED OF CHECK THE THYRISTOR MODULE (HIGH CURRENT)
For 7.5kw star delta starter how to calculate 1. Mccb rating 2. Contactor rating 3. Over load relay rating
why transformer is rated in kva instead of kw?
what is consequences of neutral and earth connect?
What is the difference between ground & earth or neutral
what is the relation between size of the anteena and wavelenghth of radiated wave
I need model question papers for RRB section engineer Chennai... Please send to my E-mail Id:- maitheerainbow@gmail.com