what do you mean by mf of energy meter & its formula?
Answers were Sorted based on User's Feedback
Answer / sagar parmar (getco)
this one is the correct formula, sorry for previous mistake
Multiplying Factor = (yard CT Ratio x yard PT ratio)/(Meter
CT Ratio x Meter PT Ratio)
| Is This Answer Correct ? | 45 Yes | 4 No |
MF means the Multiplying factor.
Its nothing but the CT ration . as a big amount of the
current to be measured So direct Metering is not possible
hence CT operated meter is used
Formula :- if the CT ratio is 60/5 then metered reading
should be multiply by 12 which give the exact Power usage
| Is This Answer Correct ? | 28 Yes | 8 No |
Answer / sagar parmar (getco)
Multiplying Factor = (yard CT Ratio x yard PT ratio)/(Meter
CT Ratio x Yard PT Ratio)
| Is This Answer Correct ? | 14 Yes | 6 No |
We normally make oil soak pits under Transformers. Oil from soak pit goes to collection pit. We provide granules/pebbles under transformers. My question is weather granules/ pebbles to be filled in soak pit or not? if yes upto what level?
What is basic difference between Soft Starters And VFD drives?
Whats the minimum value for I.R. that can be allowed for HT & LT alternators for operation?
If I fill the form of engineering services and I left the exam de to navoidable reasons . Will it counts my one attempt
what is the switching substation
33kv substation lay out details & line to line & line to earth measurements
What is the minimum permissive IR value for LT & HT motor for safe starting?
what is NGR in generator?
Dear Sirs, I am a technical persons.In one of our Electrical Sub- Station, We have installed three numbers of 1250KVA ,11KV/0.415KV Transformer to feed the Factory load. We have found some abnormality. In one of our Transformers the leakeage current from transformer body to earth through earth continuity wire is almost 86 Amp but in other transformer it is (5-10)Amp. where the load current on three phase and neutral are respectively 1360Amp,1400Amp,1370 Amp & 176Amp. So please any technical person help me about the reasons of this situation and how I can rectify the fault. Moreover,I have measured the earth resistance of the Earth continuity wire which is less than 1 Ohm. Thanks Tapas Barua
Draw transformer phasor diagram.(full load,no load)
What is the formula for finding fault level of generator?
One amps in HT is equal to how manys amps in LT
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)