Answer / murali -inst.technologist
if range of transmitter changes in field you have to change
the span of the AI in dcs
other wise
transmitter shows correct reading in field side
but dcs get signal in form of 4-20 ma, then flow reading
shows in DCS is as per old DCS span.
Is This Answer Correct ? | 12 Yes | 1 No |
Answer / www.islamqa.com
we have to configure the range in dcs with the new values.
example:
old range:
o - 625 "wc means 4ma at 0, 20 ma at 625
new range:
0 - 2500 "wc means 4 ma at 0, 20 ma at 2500
Regards,
Ahmed Sabry
Control and Instrumentation Engineer
GPC - General Petroleum Company
ahmedsabry.online@gmail.com
CELL.: 00 2 0121367310
Is This Answer Correct ? | 8 Yes | 0 No |
what is actual drum level and compensated drum level?
CONTROL VALVE OPERATING IN MANUAL BUT NOT IN MANUAL. WHAT SHOULD BE THE PROBLEM ?
Why is the orifice tab provided?
What are the materials available to prepare individually for competetive exams in Instrumentation field? Plz reply...
what the differant between Wet Leg /Dry Leg
What is a PID controller and how can it to applied to our everyday life?
Can we used Condensate Pot on flow transmitter which is using on liquid having sluge and DP transmitter is in pit and below the process line,Can we used Condensate pot for accamulate the Sluge?
what are the inputs (drawings) we need to prepare loop schematics??
what is instrument termination
What is the difference between precision and repeatability of any instrument. Why it is measured always in percentage
WHAT ARE MAIN DIFFERENCE BETWEEN DCS AND SCADA?
7 Answers ABB, Gold Fields, Rand Water,
can i calibrate DP transmitter online (while Tx in Service) if yes ,how?