can we identify the direction of power flow in transmission
line by after only looking the tower
Answers were Sorted based on User's Feedback
Answer / jitendra pawar
We can not identified what is the direction of power flow
in transmission line by after looking the tower because
tower and line from incomer and outgoing both are similar
it's not idendical.
Is This Answer Correct ? | 13 Yes | 5 No |
Answer / manoj kumar singh
Yes: The phase indicating plates installed on the tower are
always facing towards the sending side.
Is This Answer Correct ? | 8 Yes | 1 No |
Answer / mustaan
Yes: The phase indicating plates installed on the tower are
always facing towards the sending side.
Is This Answer Correct ? | 5 Yes | 3 No |
Answer / manoj sharma
asin single ckt in the dirn of danger plate
in double ckt this pricpl doesnt follow as pwr
flow in both dirn in double ckt
Is This Answer Correct ? | 1 Yes | 3 No |
Answer / gulab chandra
The phase indicating plates installed on tower are always facing towards load side.
Is This Answer Correct ? | 1 Yes | 5 No |
In transmission line 11kv,33kv etc are rms values are peak or others??
Dear all,recently in our plant we installed a conveyor for this the motor ratings are 5 hp and Amps 7.39.Due to on urgent starting of conveyor we fix the DOL starter with range of 9-15 amps.give me suggestion regarding on this issue
According to IEC60034-14, When the vibration monitoring system required for motor Bearing. above which KW, it is required? and for what type of bearing the vibration probe is provided.
We have 750KVA DG set, we want to introduce REF relay with 1250/1A,CL PS,Current transformers.The lead distance of 2.5mm copper flexible cable from CT to relay is around 5mtrs.We would like to know the knee point votage(VK) & IM calculion for CT's
how you taken aotitude test
What is the meaning of Fault level rating?
1 Answers Balrampur Chini Mill,
True or false question. 1.The fuse provide phase and neutral 2.power loss in electrical circuit can take place in (resistance or inductance or capacitance). 3.two phase system each phase has separated by a phase difference of (90 or 180 or 270 or 45). 4.3 phase balanced star connected load neutral current shall be (line current or phase current or zero or unity)
i need to now what will be the cable size to the following load, transformer to distribution panel distance 110m, load 1000kw, voltage 400v, pf 0.85, permissible voltage drop 2.0%, overhead line, atmospheric temperature 35 degree c.
0 Answers Bay Fishing Corporation,
What happened when the field winding of dc series motor is open?
How Can you do Maintenance of ACB of 2000Amperes
what is AVR and tell principle and working?
10 Answers ITC Infotech, MIOT Hospitals, YCC,
what is the definition of Nominal current or voltage