Two alternators say 1 & 2 are poised to parallel operation.
But at the time of paralleing alternator 2 gets out of the
system by tripping Earth fault relay. Please send me reply
why this is happening?
Answers were Sorted based on User's Feedback
Answer / jyotirmoy das gupta
The answer depends on the following parameters: 1. At which
point the two generating systems are earthed, 2. Is there a
neutral isolation for the second generator, 3. how the
earth fault sensing element is connected- by 3 phase CT
forming residual circuit or direct measurement placing the
CT between generator star point and earth, 4. what is the %
setting for earth fault protection and what delay is
setted.
Is This Answer Correct ? | 3 Yes | 1 No |
In addition to the above answer, what type of earthing is
provided for both the generators also matters. Secondly, if
it is NGR, which NGR is closed, or both are closed.
Is This Answer Correct ? | 1 Yes | 0 No |
Is it true online ups having bypass mode if it is true then why we called ups because it is interrupting power when goes in bypass mode
in a plug point why the hole size at the top is large?
Does the motor power displayed on the Motor name plate is the mechnical power motor delivers or it is consumed power from the system?
Which element has power dissipated in it when the source is removed ?
Define reserve-generating capacity?
Why we are putting off the APFC(automatic power factor control) panel while the generator is running?
what is servomechanism?
why we condut tan delta test i want brief explain?
how to get electrical supervisor competency certificate in gujarat. i did 3 year diploma in electrical
why did lightening arrester rod probe sharp?
What is the relay function?
how to Select Lighting arrester? What r the parameters to be considered for the selection of Lighting arrester ?