How to calibrate DP tramitter in flow measurement
application? consider my range of flow is 0 to 2000 kg/hr ?
please give calculation of , How much pressure applied on
low pressure side and high pressure side please give detail
of calculation ....
It so important for me please reply as soon as possible
Answer / suresh agravat
0 to 2000 kg/cm2 range
Formula:- URV-LRV=Span/4
2000-0=2000
2000/4=500
0=4mA(0%)
500=8mA(25%)
1000=12mA(50%)
1500=16mA(75%)
2000=20mA(100%)
Is This Answer Correct ? | 0 Yes | 1 No |
why we are using boosters at glass furnace is there any other thing?
if my flow is 20000 m3/h than which range of DPT i have to use????
what is the thermocuple compensation circuit
Capacitance, resistance ( colour coding ), parallel & series circuits.
What is the difference between PLC and DDC?
Thermocouple is a transducer but rtd is not transducer why? Both taking heat as a input and giving mv
pl give the guidance for DUBAL written test
I have a LT of 10000mmwc range. can i use this LT in 1000mmwc range of tank?? if yes than what happened???
What is derating factor in Motor?
A valve in series with an orifice plate (DP transmitter), is aligned for constant pressure in the pipeline, if there is an error dx, How to align it in process.
control panel design guidelines
what is pyrometer? which purpose it has to be used?