Golgappa.net | Golgappa.org | BagIndia.net | BodyIndia.Com | CabIndia.net | CarsBikes.net | CarsBikes.org | CashIndia.net | ConsumerIndia.net | CookingIndia.net | DataIndia.net | DealIndia.net | EmailIndia.net | FirstTablet.com | FirstTourist.com | ForsaleIndia.net | IndiaBody.Com | IndiaCab.net | IndiaCash.net | IndiaModel.net | KidForum.net | OfficeIndia.net | PaysIndia.com | RestaurantIndia.net | RestaurantsIndia.net | SaleForum.net | SellForum.net | SoldIndia.com | StarIndia.net | TomatoCab.com | TomatoCabs.com | TownIndia.com
Interested to Buy Any Domain ? << Click Here >> for more details...


why the steam drum and deaerator level transmitter range is
in negative MMWC to zero

Answers were Sorted based on User's Feedback



why the steam drum and deaerator level transmitter range is in negative MMWC to zero..

Answer / valluri066

Range is Negative mmWC to Zero because we are using "Wet leg configuration" arrangement. In which LP side of transmitter is contains a Condesate Pot always filled-in with water.

Wet leg configuration is used when the tanks contain CONDENSABLE VAPOURS, these vapours when entered impulse lines may be condensed over time and get accumulated. This accumulated liquids in impulse line creates Pressure head resulting error in level measurement. to avoid this suituation we initially fill LP side impulse line with water ( or a condensate pot is used to condense vapour and fill impulse line automatically).

Is This Answer Correct ?    7 Yes 2 No

why the steam drum and deaerator level transmitter range is in negative MMWC to zero..

Answer / mithilesh kumar

actually wht happen there..
level is totally depend upon vessel/drum/tank type..
means that it is open or close..
if it's open then range is in positve..
but if it's fully closed then range is start with negative..
by using level formula..
u can mail me if this formula or step is required..
email id: mithilesh.barnwal30@gmail.com

Is This Answer Correct ?    5 Yes 18 No

why the steam drum and deaerator level transmitter range is in negative MMWC to zero..

Answer / sam

In both cases you are using a wet leg configuration with the
DPT. In the steam drum if you use the old fashion way by
changing the HP and LP legs around you will get a positive
mmH2O reading. If you use a piped SMART Tx or a SMART
capillary type DPT, you will get this negative mmH2O readings.
I have already done a writeup on this so go and look at
previous questions.
In the deaerator there is a vacuum but again the same wet
leg is done. I have already done a writeup on this vacuum
applications as well so go and look at previous questions.
Good luck

Is This Answer Correct ?    7 Yes 30 No

Post New Answer

More Instrumentation Interview Questions

WHAT IS THE DIFFERENCE BETWEEN PLC AND DCS

55 Answers   ABB, Adani, Adani Power, GMR, IIUC,


what is orifice plate? Give me best answer?....plz

5 Answers  


why to use 3 wire at RTD ? what's the reason for common wire ?

4 Answers  


i want the equation of this question. Tranmitter range is 120 mmwc and dcs flow range is 1700 nm3/hr. if i want to change dcs range from 1700 to 2400 nm3/hr then how much dp i have to enter in transmitter

2 Answers   GMR,


Name four general (not technical) criteria that would you consider important, when deciding upon a particular control valve?

1 Answers  


why use on -off control valve in glove valve

1 Answers  


capillary type tranmitter using remote seals and capillary tubes filled with liquid of known of known density so if you wanna callibrate it just close block valve just before capilary @ high side & connect druck apply it's calibrated range pressure as normal calibration ensure low side block valve must be closed & if you asking commissioning so this is not a DP type pressure tx so simple if you wanna put in servie this tx just open high side block valve & than low side block same way i do it but still transmitter showing -13 ma.just tell me what i want to do ?

1 Answers   Gasco,


How to calibrate and check thermal mass flow meter of Make thermal instrument company inc model 60?

1 Answers   Wood Group,


if we put any thermocouple on a table in a room without any connection,what temperature should it show.

3 Answers  


What is offset in a control system.

2 Answers   Sabic,


Dead weight tester & comparator for calibration , which is more accurate , what is the application.

1 Answers   Bapco Bahrain Petroleum Company,


What is live zero and dead zero

2 Answers  


Categories
  • Civil Engineering Interview Questions Civil Engineering (5086)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4456)
  • Electrical Engineering Interview Questions Electrical Engineering (16639)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)