How can we calibrate pressure and flow transmitter in the field(online)?..

Answer / sam

This procedure can be used to calibrate any type of
instrument in the field on a live plant regardless of it's
type or application. The only variation in the procedure is
what test equipment you will use to calibrate the instrument
with. For instance calibrating a temperature transmitter you
want to take a HART and decade box with you. Calibrating a
pressure , flow or DP transmitter, you want to take a HART
and pressure pump with you like a Druck or hand pump with a
precision gauge on.
The procedure:
Since the transmitter is on line and on a running plant, you
need to determine a couple of things first before you start
working on it. First and most important of all, what does it
do? Is it a control transmitter, a trip transmitter or just
a indication.
Control transmitter means it's output will go to the DCS and
is linked to a PID controller which will give a continues
output, based on this input, to a control element in the
plant plant like a control valve or a heater element. These
are all critical control components that will trip the plant
if you upset their stability.
Trip transmitter means that it is linked to the ESD system
and will start a plant shut down if it is seeing a to high
or low pressure, flow, DP or level depending on the
application you are working on. Just indication means that
it is completely safe to work on and you cannot trip anything.
To make the control transmitter safe to work on you need to
put the DCS PID controller in manual. This will keep the
output of the controller at the current output position and
bypass the output function of the controller. In a fast
moving application the control room operator will send a
field operator with you to control the control valve
manually with it's hand wheel while you work on the control
transmitter.
To make the trip transmitter safe to work on you need to put
a inhibit in the ESD system output trip function of the
transmitter. This is also sometimes refer to as a MOS
(maintenance override switch).
In both cases the control room operators will do this for
you providing that you have all the permit to work and
inhibit permission paperwork in place.
Good luck

Is This Answer Correct ?    34 Yes 10 No

How can we calibrate pressure and flow transmitter in the field(online)?..

Answer / pangavenkatesh

How to calibreate dp transmitter

Is This Answer Correct ?    8 Yes 0 No

How can we calibrate pressure and flow transmitter in the field(online)?..

Answer / anjal

first close the isolation and open the equaliser if its
show zero ok other wise calibrate the transmitter

Is This Answer Correct ?    18 Yes 12 No

Post New Answer

More Instrumentation Interview Questions

where cascade loop use ?

0 Answers   KNPC, KOC,


for indiacation of turbine(china) bearing temperature what type of sensor will be used(i.e. rtd or thermocouple or themister ) ? why it is ? i need clear explanation ?

2 Answers  


Can any body help to get Rsemulator 5000 free from internet if possible then give me any link or any help .

0 Answers   Engro,


i hav applied for the post of engg. in iocl so please require the past test papers fro instrumentation engg please please help me and send me the papers or tell me the pattern and type of ques asked in examination......

0 Answers  


what is the meaning of HART ?

2 Answers  






why is honed type flow orifice plate? what purpose it used? how to select this?

4 Answers  


generally transmitter power supply having some range(12v to 35v) but the out put(4-20 mA) must same for given input.If we vary the power supply voltage then output mA also to be change according to V=IR. Is there any voltage regulator in the transmitter ?

2 Answers  


My friend has faced this question! I don't know clearly. So please anyone give me the correct and short answer to this question? What is variable frequency drive? Types, what is star to delta? Why this arrangement necessary?

5 Answers   Asian Paints, TCS,


What are the Components of Siemens S7 300 Series PLC system ?

1 Answers   Siemens,


how to rectify the poor signal strength in utrasonic digtial flow meter ,model:ge digital xce868i

0 Answers   KNPC,


How an rtd work, and what volts/current goes to a rtd to measure the resistance?

0 Answers  


I want to measure flow by using DP Tx and range is 0 to 1200 Kg/cm2 ?

2 Answers  


Categories
  • Civil Engineering Interview Questions Civil Engineering (5085)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4451)
  • Electrical Engineering Interview Questions Electrical Engineering (16632)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)