why we use 24v dc in instrument rahter than 230vac????
Answers were Sorted based on User's Feedback
Answer / visakh ctjv
all loop powered transmitters are capable of
withstanding 10 t0 36v dc ...as per the process requirement
it will vary.. insome industries they are using 12v dc
also.. 24 vdc is used because as per ISA there are some
standards wich will match other process reqirement like
24vdc relays for digital control also wecan use 24dc to
energize tis relays
Is This Answer Correct ? | 22 Yes | 7 No |
Answer / sanjay goswami
24 VDC potential is safe for use in Oil& Gas industries,230
VAC has hight voltage potential and therefore posses high
risk energy for Oil&Gas and human working on it.
DC power is also clean and does not contain any noise like
AC,therefore for precise instrumentation 24 VDC is the
suitable power.
Is This Answer Correct ? | 9 Yes | 0 No |
Answer / mohammed abbas
INSTRUMENTS ARE DESIGN TO WORK ON LOW VOLTAGE BY THE
MANUFACTURER LIKE,YOKOGAWA,HONEYWELL AND ROSEMOUNT.LOW DC
VOLTAGE 24 VDC WHICH IS COMPITIBLE FOR ALL THE CONTOL
SYSYTEM AND THE FIELD INSTRUMENT WHICH IS DESIGN WILL WORK
ON 24 VDC WHICH IS REQUIRE TO ENERGIES THE ELECTRONIC PART
ALSO.IF WE USE 230VAC MEANS IT IS DANGER BECAUSE WHICH WILL
CAUSE A ACCIDENT OF LIFE ALSO IF ANY UNSKILLED TECHICIAN
WORK ON THAT INSTRUMENT.24 VDC IS SAFE FOR HUMAN BEING AS
WELL AS LOW POWER CONSUME,WHICH IS COMPITBLE FOR ALL THE
CONTROL SYSTEM AND ALL THE INSTRUMENTS IS BUILD WITH
ELCTROIC WHICH IS FUNCTIONING ON LOW 12 TO 32VDC.ALL THE
INSTRUMENT DESIGN IS ON THE BASIS OF LOW VOLTAGE AND LOW
CURRENT ONLY.
Is This Answer Correct ? | 12 Yes | 5 No |
Answer / narendra mishra
the max voltage is 24v & max current flow throw cable is
27mA so max power loss that cable can bear is 647mW.which
is allowable for the cable designed .
Is This Answer Correct ? | 4 Yes | 2 No |
If The RTD(PT100) Show .776 Kohm Resistance the Temperature of process fluid how much?
What is exact difference between the panel earthing and system earthing in DCS system. What is the value of resistence.
what is the principal of coriolis mass flowmeter
PLEASE PROVIDE SAMPLES OF CHEVRON SKILL TESTS
A pressure transmitter with a range of 0-100 bar.The accuracy of the instrument is 1% of upper range value? The pressure indicating transmitter is showing the system pressure is 50 bar. b. When you include the error, what is the minimum possible pressure in our fuel gas system? i. 49.5 bar ii. 49 bar iii. 1 bar iv. 0.5 bar We want to change the filter cartridge. We must depressure the fuel gas system. c. After we depressure the system in preparation for maintenance, the transmitter displays a pressure of +0.1 bar. At this time, what is the possible range of pressures in our fuel system? i. +0.099 to +0.101 bar ii. 0 to +0.2 bar iii. -0.1 to +0.3 bar iv. -0.9 to +1.1 bar
What is super thermocoupal?
what is bevel? why bevel required in orifice plate?
how to overhaul control valves.what are the proper procedures.
Explain why use mmwc unit?
WHAT IS THE CAM POSITION IN CONTROL VALVE POSITIONER ? WHY IT IS USED?
We have yokogawa cs3000 one fcs and 4 his. After download to his, showing successfully at es, but not transferred to his.
In Boiler Drum Level- Level control valve how can it tuning (PID)?