Can a 50-Hz designed transformer be used at 60-Hz system?
Is the same remains true, when a 60-Hz designed transformer
be used at 50-Hz system? Consider only frequency variation.
The voltage remains as rated value in all cases.
Justify the answer.
Answers were Sorted based on User's Feedback
Answer / iamdon
A 50-Hz designed transformer can be used at 60-Hz system
but a 60-Hz designed transformer cannot be utilized at 50-
Hz system.
Because in later case, the transformer windings(primary and
econdary)will draw approximately 20 % greater current than
the rated one.More current flowing will produce more
winding heating loss.The temperature of winding rises
(Beacuse cooling system was designed for rated current
which was lower as compared to present higher value of
current at low frequency operation)and it get burnt.
Author:arbelectbit@yahoo.com
Is This Answer Correct ? | 8 Yes | 3 No |
For a transformer the voltage is proportional to the product of flux and frequency.
case-I
Voltage = constant
Frequency = increased from 50 to 60Hz i.e. change by 120%
For Transformer:
Voltage = flux * frequency * K; k is a constant
so when frequency increases by 120% flux decreases to 83.3% Now;
Hysteresis loss = flux^2 * frequency^2 * T; T is constant
At 50 Hz
Hy. Loss@50 = flux^2 * Frequency^2 * T
At 60 Hz
Hy. Loss@60 = (.833flux)^2 * (1.2Frequency)^2 * T
On evaluation:
Hysteresis loss@50Hz = Hysteresis loss@50Hz
Eddy Current Loss
Eddy C. L. = flux^1.6 * f * C; C is a constant
Eddy@50 HZ = flux^1.6 * f * C
Eddy@60 Hz = (.833flux)^1.6 * 1.2F * C
On evaluation;
Eddy@60Hz = 0.895 * Eddy@50HZ
So it is seen that a 50HZ transformer when operated at at 60Hz has same hysteresis loss eddy current decreases. As the core loss decreases the transformer can be safely operated.
But if a 60Hz transformer is operated at 50Hz, then just the reverse of above the core loss i.e. eddy current loss will increase and hence the core loss will go high; hence not advisable to operate.
Is This Answer Correct ? | 0 Yes | 0 No |
What happen if we apply square wave or traiangular waveform voltage to the transformer primary winding instead of sinusoidal wave?
Which type of moter is used in trains, what is the ratting of supply used explain Working principal?
Is there any local or International standards that prohibit the installation of earthing pit in the planters area where the earthing pit is subject to continues soak in water?
why the generator operating along with the infinte bus bar should never be under_excited?
can anyone tel me what is competency of electrical supervisor??
Which type of material used for fuse wire & solder wire.
why capacotors burnt out
what the main difference of the 3 phase and 2 phase power supply??
Why do we apply both Differential and REF (HV and LV) protection schemes on YNyn configuration of a transformer?
The SFC of an engine is 0.25 kg/kW hr. when the fuel used has a calorific value of 36000 kJ/kg. the thermal efficiency of the engine is
what is ATS?and its function or operation in power system with its layout.
what is differentila pilot supervision in the incomer control panel in the power station?