i am working in thermal power plant .
if temperature transmitter is not showing reading in dcs
then how can we rectify the problem?
Answers were Sorted based on User's Feedback
Answer / k.sreenivasan
Go to the field and check the local indication in the
transmitter.(normally it is in either engg. units or as
percentage)
If it is zero ,then the problem is in the sensor or
terminal connection, because most of the current generation
transmitters are highly accurate and have longer stability
periods.
Suppose local reading is ok,then check the DCS analog input
card for any fault condition and clear it.Normally this
situation is rare.
Is This Answer Correct ? | 24 Yes | 1 No |
Answer / s. kanniyappan
Check the Sensor properly. if it is ok, then
1)check continuity between the sensor cables
2)tight the cables properly
3)check the transmitter supply (24vdc)
if it is not ok, then check the DCS analog i/p cord.
Is This Answer Correct ? | 14 Yes | 0 No |
Answer / k.manikanta naidu
check the millivolts output of thermocouple.then multiply
with the standard values depends on the type of
thermocouple.if the value is ok,check the temparature
trnsmitter,then check the mA o/p of TT.
Is This Answer Correct ? | 8 Yes | 0 No |
Answer / g kiran kumar
1. Check the wiring at all terminal blocks at field, at
control panel and at PLC for any loose connection.
2. Check the Transmitter supply.
3. Measure the output from Transmitter.
4. Check cable continuity.
5. Finally check the configuration of TAG in the DCS (may
be someone deleated accidently).
Is This Answer Correct ? | 6 Yes | 0 No |
Answer / satish
SEE THE FIRST ALRM CONDITION ON TRANSMITTER BECAUSE MOST
PROBABILITY IN PRIMERY ELEMENT PROBLE.
Is This Answer Correct ? | 6 Yes | 3 No |
Answer / pradeep kumar
check the tt reading once again check the main cable (from
element resistance or mv)and also check the branch
cable(from dcs 24 v)its available the problem in dcs side
check the analog modules
Is This Answer Correct ? | 1 Yes | 0 No |
I want to install analog type, flange mounted gas flow meter (line size - 2"), for CNG flow measurement.Kindly give some details of flowmeter or suppler name, available in India.
defination of plc? why we use plc? application of plc? advantage of plc?
what would be the minimum flow rate that we can measure on rotameter..?
why we use 4-20 mA to do calibration of the instruments.why we cant use 0-20 mA?
NSV type probe stands for
FOR CO/CO2/O2/NOX applications which of the following manufature is best? and what is the basic principle of gas analysers? ABB/YOKOGAWA/EMERSON/SIEMENS/TELEDYNE/THERMOFISHER
In control valve there are two type of valve seat we can use metal to metal seat & soft seat.On this valve seat i have following doubt. 1)I have never seen practically the internal assembly of valve so my doubt is that basically weather the seat is soft seat or metal its basic MOC is same as valve body(SS or CS) only in soft seat we are using PTFE ring & place on valve seat & in metal this PTFE ring is not threr am i correct??????? 2)what are the common general rule for using metal to metal seat & soft seat,means its depend on process parameter like liquid,gas, steam & on valve leakage class.
What is negative range in transmeter?
why we use by pas on a positioner? When can a by pass be not used on a positioner ?
what will be the output of a temperature transmitter if temperature is 120 degree celcius?
what does 5/2 solinoid valve means?
What is surge in compressors? How to detect and control it?