Why 3 over-current and 1 earth fault relay is used on
primary side of transformer? Why 2 over-current and 1 earth
fault relay in used on secondary side of transformer?
Answer / ronik
1)The reason when a double line fault occurs on secondary
side then if the transformer is of DY11 type then if 2
over-current relays are used on primary side instead of 3
O/C relays then the phase in which no relay is placed will
carry double the fault current and the in current in the
either phase will be low enough that a relay can pick
up...and meanwhile the damage will be done to the system...
2)Moreover the ground fault on the secondary side will not
have any effect on the earth fault relay on the primary side...
3)on secondary side each and every fault will be detected by
the 2 O/C and 1 earth fault relay easily...
Is This Answer Correct ? | 4 Yes | 4 No |
what is insulation percentage of motor 3 phase and singlephase
Why front mounted CT polarities are always towards breaker?
Why transformer rating in kVA not in kW?
15hp motor wound by 0.9mm & 0.95mm magnet wire. at no load test it draw 4.2A current. Another motor with same condition draw 9.2A current. How can that occur? pls help
What is the difference b/w fanuc alpha series 16i and 18i controller. what is stand for i
what is transient stability analysis means?
What conditions are required for a transformer to operate at low frequencies ?
what are the different kind of cables used for transmissions?
11 KV distribution system where neutral is produced ?
4 Answers ciss, TATA, Tata Motors,
In what voltage EHT works(133/132/33/66kv?
What is the range of efficiency of thermal or steam power plants? Why it is so low?
A T-T transformer can not be parallel with transformer A V-V B star-delta C star-star D delta-delta