What are the factors to be considered during the
Synchronization?
Answers were Sorted based on User's Feedback
Answer / ganesan.n
1. Phase sequence must be the same,
2. Voltage Must be the same,
3. Frequency must be the same.
Is This Answer Correct ? | 7 Yes | 0 No |
Answer / hari hajare
During Synchronization Following Parameter Must be Match
With Other Source
Voltage,Powerfactor,Frequency,Phase angle
Is This Answer Correct ? | 4 Yes | 0 No |
Answer / yogesh singh
1. Frequency must be same
2. Voltage must be same.
3. Phase sequence must be same.
4. Transformer vector group must be same
Is This Answer Correct ? | 4 Yes | 0 No |
why we use single core 630mm2 cable for transformer secondary side
Is 3C x 2.5 Sqmm Cable can withstand 40Amp Starting current? If Yes then specify your ans.
what kn of disc is used in 33kv,132kv,220kv,400kv,800kv transmission line
why mccb is not tripping when phase & neutral terminal are interched ?
how is find out kwh step by step
what is the formula to calculate the fault level current for any substation?
what is the healthy specific gravity of lead acid battery used in DG sets ?
3 Answers Bhushan Power Steel,
what is emitter follower configuration? and what are it's features?
What is Harmonic affects in power system. what is unit of harmonics and how to measure it. how much value should be in power system.
On load tap changer (OLTC) explode? Transformer Vector group: Ynd11 Rated Power: 353MVA Rated Current: 693A Voltage:294/20KV OLTC Type: T III Y1000 110/c 12193w Max Operation Current: 295A Step Voltage: 550V Arrangement in Tx windings: Y Connection Problem: Damage of Unit 1 Generator Transformer On Load Tap Changer (OLTC) Description of Incident: 9.00 a.m. :- Generator No Load test on excitation system started 10.30 a.m :- Carried out AVR change over test 11.30 a.m :- Preparation for Generator Manual Synchronizing test 12.00 a.m :- Manual Synshronizing test started. Observed incoming generator voltage higher than running voltage. CECR operator operated Generator Transformer OLTC to bring down the incoming generator voltage 12.03 a.m :-Generator Transformer abnormal alarm operated at Gen.Control Desk (CECR) CECR operater at Generator transformer bay informed that the transformer oil splashed out from OLTC. CECR operater informed that he heard explosion inside OLTC. Observed Oil level & Oil Flow alaram operated at Tranformer local annunciator. 12.05 am :- CECR operator 'Open Gen Field Breaker” 12.10 a.m. :- Elec1 team inspected the OLTC and found the OLTC rupture disk was broken and oil spilled at OLTC area. - Elec1 found the OLTC top cover bulging. Do anyone know why and possibility cause happen in this OLTC.
what is sevice settings for mccb?How can be it setted?
why in transformer there is not rotating fiddl/ magnetic field like motor